    Yes I am splinter, and I could tell the NICEIC , Electricians Forum, and Jack Splinter and his big stick, where to shove a great deal of it, you don't hardly register on the numpty scale, cos you are are messing about on yer mums lap top , noe SWITCH IT OFF before I send Lucia in to smack yer erse
     
  3. mr reflex

    mr reflex Member

    Last orders in the playground mr wheels, your call.........
     
  4. mr reflex

    mr reflex Member

    To all posters, I think it was quite apparent what the call was.........delete, delete, delete
     
  5. spinlondon

    spinlondon Screwfix Select

    Well lok, whenever you measure Ze, you should disconnect the bonding, otherwise it's not Ze but Zs that you are measuring.
    Being experienced and qualified, you should already know this.
     
  6. mr reflex

    mr reflex Member

    You are now officially talking to someone who is not there....... Doctor.........
     
  7. Lokkars Daisy

    Lokkars Daisy New Member

    Nah ,carry on , **** all else here since Mr Horse put his ignorant hoof in , besides mr handy andy's (why doesn;t the voltage increase') still standing .remains tgo be toppled
     
  8. removed 7

    removed 7 New Member

    spinlondon: what a sad little man.......
     
  9. mr reflex

    mr reflex Member

    Correction, "boy"......
     
  10. Lokkars Daisy

    Lokkars Daisy New Member

    /on onlijhI don't know if I can keep this up.h  kug it's murder , on the dance floo r and fifficult to psoytvb  from mn phone1 b  
     
  11. removed 7

    removed 7 New Member

    Blimey Lockheart, Andy's thread went to 900+ posts - with a little help from his friends.  Do you seriously think we can play around with this idiot spinster that long? Pffffttttt!
     
  12. Lokkars Daisy

    Lokkars Daisy New Member

    Is this a kinda reverse predetator thing, a sort of anti grooming thing, I can't beleive you are 80plus    nah ! you surely are;nt 80 plus..are you ? nowt wrong if you are , i'll still like you
     
  13. Lectrician

    Lectrician Screwfix Select

    Although, if you go by the NIC recommendations, it is actually called Zdb.  It is permitted to carryout Zdb instead of Ze during an EICR for practicality reasons (depending on site).  If you can isolate the site, then a Ze should be done, but if you are unable to isolate, you can measure Zdb.
     
  14. unphased

    unphased Screwfix Select

    Yes, Lec. spin thinks the 'db' stands for disconnected bonding.
     
  15. spinlondon

    spinlondon Screwfix Select

    Zdb is a term used to describe Zs when measured at a DB.
    It is not a term used to describe Ze.
    On a site with multipe boards, Ze would be measured at the origin of the installation, and Zdb would be Zs measured at secondary boards.
    I assume from Unphased's comment, that he was also unaware that Ze is measured with bonding disconnected.
     
  16. Bazza-spark

    Bazza-spark Screwfix Select

    No requirement to measure.  Can be ascertained by enquiry or from previous documentation where available.

    Kind regards

    BS
     
  17. spinlondon

    spinlondon Screwfix Select

    Yes Bazza there is no requirement to actually measure Ze.
    Not certain that anyone has said that there is a requirement to measure.
    That aside, if (even though you don't have to) you were to measure the Ze, the measurement is conducted with the bonding conductors and CPCs disconnected.
    This is done to remove any parallel earth paths that could affect the measurement.
    I would be wary about relying on the information contained in previous documentation.
    The older the documentation the more wary I'd be.
    There are a number of reasons why Ze is measured.
    One is to verify that there is a distributor's earth.
    Another is to determine whether the distributor's earth has deteriorated, or in some cases improved.
     
  18. Lokkars Daisy

    Lokkars Daisy New Member

    Listen pilondon , I know all the ins an outs , I whimsically posted the above to taunt you:) 
     
  19. Lokkars Daisy

    Lokkars Daisy New Member

    Yes I know, did you notice no one else picked me up on that :)
     
  20. spinlondon

    spinlondon Screwfix Select

    Did you now, a bit childish if that was the real reason.
    Of course if you did know the ins and outs, it begs the question: Why did you ask Seneca about it?
    Yes I did note that no one lese picked up on it.
    Could be that no one had noticed yet, or could be that they didn't know themselves.
    Could be a bit of both.
     