Hi Everyone,

I have purchased a brand new Hotpoint HAE60KS electric cooker from Curry's.
I was told I would need to purchase the electrical cable for it myself however I do not even know where to begin looking for the cable. I have the connection point for it on the wall with the usual LIVE, NEUTRAL & EARTH terminals.

I have contacted Hotpoint to see if they can shed any light on it but they are clueless.
I have a friend who will install It for me but to save him time looking for the cable I thought I would just get it myself and let him install it.

Thanks in advance for all usable advice. I hope I have given enough information here to help.
 
Is there a circuit breaker in your consumer unit marked up as 'cooker, if so what ìs it's rating, 32a (amp).
What is your new cooker rated at in watts or kw (kilowatts), these things at a very minimum are required before we can give any more help tbh.
 
Hi everyone, thank you for all the great advice, at the circuit board it has a switch with "cooker" below it and says "B32" if that means anything?
 
Firstly I am not saying the 6mm cable is wrong - however this cooking unit can be moved to say clean around the back of it etc and of course this moves the cable and the unit cannot be classed as static. I would have thought that within regs the use of 6mm would be in question due to the limited amount of flexing it will take before the solid cpc snaps, in other words cable should be used which allows for movement. This means stranded heat resistant flexible round which as far as I know is not available in 6mm upwards.

Only an observation, and I know in reality the 6mm t and e is always used.
As a point of note 10mm is course stranded in all conductors.
 
just a question at this point. The cooker is rated at 10.7Kw so by my calculation that means the maximum current in the circuit = 10700/230 = 46.5a.
Wouldn't that mean a 50a RCB and probably 10mm2 cable?
 
I would guess that the 10.7Kw rating is if all possible heating elements are on at the same time, which they never will be. You'd be hard pushed I would think to even get 32 amps draw.

Your cooker looks identical to mine except for the colour (its a Hotpoint too with ceramic hob, top oven/grill and main oven), its on a 32A MCB and had no problems. Highest current draw is when I'm starting it up, turn on the main oven and a couple of hob rings perhaps.
 
Thanks Dr Bodge - sorry m8 I was thinking of something else, please forget my silly post, and thanks for your reply.
 