What size cable for 10.5 KW shower?

Discussion in 'Electricians' Talk' started by Nigel, Oct 28, 2003.

  1. Nigel

    Nigel New Member

    And what size should the breaker be?
     
  2. supersparky

    supersparky New Member

    10mm2 will be fine 45amp mcb
    supersparks
     
  3. supersparky

    supersparky New Member

    **supersparky not supersparks a hard day of work has taken its tole :(
     
  4. RH

    RH New Member

    make sure that there's a 30mA RCD in the circuit as well.
     
  5. Mr Lucky

    Mr Lucky New Member

    and that any exposed pipework within the bathroom is bonded to all other exposed conductive parts and equipment so as to avoid a potential difference
     
  6. chtechie

    chtechie Member

    and that any exposed pipework within the bathroom is
    bonded to all other exposed conductive parts and
    equipment so as to avoid a potential difference

    I think the above should read exposed conductive parts and
    other extraneous conductive parts.
     
  7. supersparky

    supersparky New Member

    like i say and you have also---late night long day i have given exact instructions as published by the niceic in there news relese i think this will be quite adequate
     