Wiring 13A socket on lighting circuit

I didn't say I wasn't a spark, I said I didn't work as a spark. So please explain. I will understand.

Why is it bad practice to fit sockets to a lighting ctt?
Because 13a sockets are designed for loads up to 13a. Putting a 13a load on a lighting circuit will plunge you into darkness.
 
Because 13a sockets are designed for loads up to 13a. Putting a 13a load on a lighting circuit will plunge you into darkness.
If he was saying can I install a socket off the lighting circuit for a kettle then yes, but a few lights?? Don't think so
 
Put a 3a fuse in plug.
A 3a fuse has no discrimination against a 6a MCB especially when that MCB is already loaded with lights around the house.

Anyway someone about to plug in a large load is not going to stop and change the fuse for one he knows will fail.
 
A 3a fuse has no discrimination against a 6a MCB especially when that MCB is already loaded with lights around the house.

Anyway someone about to plug in a large load is not going to stop and change the fuse for one he knows will fail.

The regs say to discriminate you need the fusing factors of the fuses to be about half of each other. 6a / 2 is 3a. The time current characters will show this. Have you found a anomaly in the laws of physics?
 
The regs say to discriminate you need the fusing factors of the fuses to be about half of each other. 6a / 2 is 3a. The time current characters will show this. Have you found a anomaly in the laws of physics?
A 6 a MCB already loaded by lights around the house leaves a margin less than 6. <6a/2 is <3a.
 
Probably the only solution, someone may not agree because its a ' 3 pin socket and other things can be plugged in like toaster or tumble dryer'

Its a lighting circuit so probably protected by a 6A MCB or RCBO and if the plug has a fuse of 3A then....
Just put a label on the outlet (s) saying something like 'FOR LIGHTING ONLY' and be done with it.
 