  1. edward current

    edward current Active Member

    hi gents

    when testing a Zs reading today i got a >2000 ohm reading

    I was using the fluke 3 wire tester

    I put the neutral lead to earth and got a 0.2 reading indicating a neutral fault ??? yes ???

    I then got a 250V reading between phase and neutral indicating the neutral is ok ??? yes ???

    any views...

    All Mohm was >500 ohms

    R1 + R2 readings ok
     
  2. fooman

    fooman New Member

    hi gents

    when testing a Zs reading today i got a >2000 ohm
    reading

    I was using the fluke 3 wire tester

    I put the neutral lead to earth and got a 0.2 reading
    indicating a neutral fault ??? yes ???

    I then got a 250V reading between phase and neutral
    indicating the neutral is ok ??? yes ???

    any views...

    All Mohm was >500 ohms

    R1 + R2 readings ok



    oh dear :(

































    should have used a megger :^O
     
  3. The Electrical Yoda

    The Electrical Yoda New Member

    hi gents

    when testing a Zs reading today i got a >2000 ohm
    reading

    I was using the fluke 3 wire tester

    I put the neutral lead to earth and got a 0.2 reading
    indicating a neutral fault ??? yes ???

    I then got a 250V reading between phase and neutral
    indicating the neutral is ok ??? yes ???

    any views...

    All Mohm was >500 ohms

    R1 + R2 readings ok

    Sounds like you not the tester

    Check the battery

    Check the leads on correct wholes and Fuses intact

    Check it is set to L-PE not L-N on loop test mode

    Join all leads together and zero (Fluke can zero lead on loop mode, unlike the megger)

    Try a Ze to confirm that the tester now works

    Re-test 'faulty' circuit if still FKD then fault find as usual.

    Yoda :)
     
  4. The Electrical Yoda

    The Electrical Yoda New Member

    Check the leads on correct wholes and Fuses intact

    Check the leads in correct holes and Fuses intact

    OOps Yoda :)
     
  5. sparky Si-Fi

    sparky Si-Fi Screwfix Select

    Just a little info.

    The meter only uses the neutral to light the display

    You can test Zs at a switch drop BTW by joining neutral and cpc together and hit TEST

    Might not be relevent to your inquiry OP but might be good for future ref.

    Si
     
  6. edward current

    edward current Active Member

    Sounds like you not the tester

    Check the battery

    Check the leads on correct wholes and Fuses intact

    Check it is set to L-PE not L-N on loop test mode

    Join all leads together and zero (Fluke can zero lead
    on loop mode, unlike the megger)

    Try a Ze to confirm that the tester now works

    Re-test 'faulty' circuit if still FKD then fault find
    as usual.

    Yoda :)

    wot a good idea i never thought of that...........
     
  7. The Electrical Yoda

    The Electrical Yoda New Member

    wot a good idea i never thought of that...........

    If you know the answers, why post this in the first place.

    On this forum if you post a stupid question and make yourself look stupid, then expect a stupid answer.

    Yoda :(
     