All RCD installs

Discussion in 'Electricians' Talk' started by Coloumb, Jun 25, 2016.

  1. Coloumb

    Coloumb Screwfix Select

    So why the needs for yer bonding?
     
  2. peter palmer

    peter palmer Screwfix Select

    Because it still takes time for an RCD to trip.
     
  3. Coloumb

    Coloumb Screwfix Select

    30ms, bonding or not...
     
  4. JP.

    JP. Screwfix Select

    What happens if the rcd malfunctions Mr C? - lets say a fault develops and the rcd is faulty..mcb trip time will then become highly relevant, and what kind of mcb trip time will occur in a no bonding situation?
     
  5. nigel willson

    nigel willson Screwfix Select

    Cos the big book says you do????!!!!!!!
     
  6. leesparkykent

    leesparkykent Well-Known Member

    To limit the potential under fault conditions.
     
  7. peter palmer

    peter palmer Screwfix Select

    Well up to 300ms before its classed as a failure, that 0.3 of a second, if the kettle casing is at 240 volts and the cold tap is at 0 volts thats full mains voltage through you until the RCD trips. If the water pipe is bonded then its 0 volts through you until it trips (assuming your not earthed anywhere else).
     
  8. Paco de Lucia

    Paco de Lucia Member

    what if you're not touching the kettle and you just using the tap...or the outside tap
     
  9. peter palmer

    peter palmer Screwfix Select

    Well you will be ok, but its a good point about the outside tap, I've always said that an outside tap on a TNC-S system should have a plastic coupler on it.
     
  10. stateit

    stateit Screwfix Select

    Use a plastic kettle.
     