Bosch combi loosing pressure when heating is off

Discussion in 'Plumbers' Talk' started by Peixesapo, Apr 27, 2024.

  1. Peixesapo

    Peixesapo New Member

    Hi there
    Got a new boiler installed last Christmas. Initially we had a leak because the old expansion vessel was left and dicomissioned later as I was told boiler has an internal one.

    All fine for a few months but now the boiler is loosing pressure when the heating is off. It looses overnight too, when we didn't even use hot water.

    Can I still have a leak on the heating system or is this boiler related? I assumed the water doesn't run through the heating if it's off? I will call the company who installed it, but I want to have the info as I am pretty sure they will blame it on the house.

    I have lined up a thermal image surveyor in case it's not the boiler, but something here does not add up to me

    Thanks
     
  2. terrymac

    terrymac Screwfix Select

    Does pressure rise to around 3 bar when central heating is on ?
     
    Peixesapo likes this.
  3. Peixesapo

    Peixesapo New Member

    That is the last thing to check. I will report tomorrow. Thanks
     
  4. Peixesapo

    Peixesapo New Member

    So I tried the heating. The copper pipe at the back of the house (I guess this is the prv) is dry but the condensing pipe is wet, I guess that is it's purpose.

    Pressure went from 1.4 bar to 1.7 bar according to the boiler display, but from 1.4 to 2 according to a gauge I have on the filling loop. This was in the space of 45 min-1 hour. When turned off, it cooled to 1.6. The bag on the prv is dry.

    I inspected all the rads and the one in the kitchen has a bit that is badly rusted. Could it be than even when the heating is off, there is a pore there where air comes in? I cant see water falling underneath but it's definitely going somewhere...

    I will ring my plumber to come inspect that radiator and most likely change it...
     
  5. terrymac

    terrymac Screwfix Select

    If the system is losing pressure every day you have a leak. This could from within the boiler ,or on the system side ( pipework/ radiators etc)
     