Foil backed plasterboard causing fault.

Discussion in 'Electricians' Talk' started by iandaviot, Jul 1, 2014.

  1. iandaviot

    iandaviot Member

    Hi, just wondering if any one has come across this before.

    We have just completed at conversion of 2 flats in to 1 house and we did a complete rewire. The construction of the orginal property was concrete block cavity wall with 25mm strapping and then 9mm plasterboard. The client wanted to enhance the insulation on the house so over the existing plasterboard the joiners have fitted new kingspan backed plasterboard (30mm kingspan 12.5mm plasterboard).

    Most of our cables are run in the loft and floor space and the drops come down/up the wall between the concrete block and the original plaster board. Some have been clipped to the surface and coved over with new kingspan plasterboard in small voids (cables possibly touching foil).

    The plumber went to fit a new radatior the other day, fitted it on the wall ok connected it up but could not finish it as had wrong lock sheilds so came back next day to fit and BANG!!! When he took of radiator one of the screws was black so he thougt that he had hit a cable behind the wall. He took a patch of plasterboard off but there was nothing behind but the screw had arced of the foil tripping the lighting circuit.

    I was in today to find fault but couldnt pin point it. I assumed a plasterboard screw had gone through a cable and touching the foil making it live.
    Located as many screws as possible and they donet seem to be to close any of the cable runs.

    I did a few IR test and circuit is almost clear.

    L-N >500M Ohms
    N-E >500M Ohms
    L-E >500M Ohms

    Foil - neutral >250M Ohms
    Foil - earth >250M Ohms
    Foil - live 25-50M Ohms

    Foil - earth 5.2 Volts (any earth inc main)
    Foil - random screw 3Volts

    Earth - random screw 25-50M Ohms (any earth in main)
    Between foil and nail in concret block 5 Volts

    I thought of 2 possible senarios

    1. Screw had been touching live cable but now blown clear
    2. Induced voltage (but could this be enough to blow the mcb?

    All circuits RCD protected.

    Any thoughts would be appreciated.
     
  2. Mr. Handyandy

    Mr. Handyandy Screwfix Select

    'tripping the lighting circuit' ?

    Do you have light switches with metal backboxes in the foil-backed p/b ?

    Mr. HandyAndy - Really
     
  3. MGW

    MGW Screwfix Select

    I think of the Emma Shaw court case which started 2007 and was only finished this year OK today we have RCD protection so could not happen that way but the report on how the fault had blown clear and in doing so lost earth completely and then she was killed a year latter after a water leak makes me say the fault has to be found.
    With consideration of the above even I would be testing every switch earth connection to ensure no earths have been lost during the event.
    As to what to do if you can't find it at the switches that becomes hard. But I am sure you don't want to have to stand where Mr Hoult stood and be blamed for a death.
     
  4. Bazza-spark

    Bazza-spark Screwfix Select

    Hi Ian

    Very difficult one. Guessing with it being light the probability is on a drop so that will probably be a switch. Can you test back from the switches to earth/foil? Drop the switch plates off and test to see if you can detect anything? Th only other option I can think of would be to disconnect at the roses and see if you can isolate to a particular cable giving a lower reading.

    Hope that helps

    Kind regards

    BS
     
    FatHands likes this.
  5. iandaviot

    iandaviot Member

    Thanks for you replies.

    We have used some metal boxes but none of theses are where the foil plasterboard is. All external walls have the foilback and internals are just original plasterboard stud walls. If any boxes are cut in foilback plaster board with kingspan they are fast fix.

    The area where the radiator was to be fitted is a porch at the very bottom of the stairs. The fuse box is in a cupboard in this area, and mounted on an old bit of chipboard that is on the old plasterboard. The foil back plasterboard with king span had been taken up to the edge of the cupboard. The porch outside wall are foil backed with king span but then there are breaks with normal old plasterboard. So it not like there is continuous continiuty between the foil.

    When we were carrying out the IR testing it seemed to me that the plasterboard was conducting some how and even conducting through the likes of the chipboard. Is this even possible? Its doesnt seem damp at all which could have been a possibility.

    We took of several switches and and from the board all the way through (even passed the fault area) we were getting clear on all cables. I didnt take all lights/ switches off but may have to do this yet.
     
  6. Lectrician

    Lectrician Screwfix Select

    When you're IR testing, what are you testing between?

    Can you connect to the foil back?
     
  7. Hi Ian.

    I'm not a sparky, so the test readings you gave in your first post mean little to me - ie: I know what the 'terms' are, but not if the actual readings are good or bad.

    So, standing back and looking at this as a layman.

    You give two possible scenarios in your first post. (2) Induced voltage large enough to trip the MCB and go seriously 'bang'? No, surely next to impossible. The foil is in large, flat sheets as opposed to loops or coils of any sort; any voltages induced would be tiny. Large flat sheets do bring to mind 'capacitance', but even then the 'other' plate is a cable,which cannot be that close, so capacitance effect also would be teeny, tiny.

    In any event, if induction or capacitance were possible scenarios, there would be exploding walls all over the country.

    So to (1). I'm guessing that, if the foil backing were 'live', then the 'bang' was caused by the earthed drill bit? Ie: the drill bit/screw didn't cut through an actual cable and short two wires therein - it touched only a single conductor (the foil) so that foil must have been 'live'?

    No (1) strikes me as being the only likely scenario, in which case thank your lucky stars that this plumber happened to accidentally locate the problem - or else the potential for the customer to locate it themselves in the future using a screw and screwdriver would have been very high; imagine living with a 'live' wall? :eek:

    I can only think of one likely way this could have happened - and it's what you say yourself; a plasterboard screw nipped the live wire and turned the whole sheet live too. And it's probably also very likely that the foil was also 'blown' around that screw as you say, breaking that bond afterwards. But, it'll be close.

    (Or, the reverse happened - the plumber's drill was live and he earthed it through the foil... Nah - not likely!)

    How else could that foil have become live? Via a metal back-box? Via some weird cross-wiring in a socket/switch plate? Hmmm, surely it's almost certainly a p'board screw?

    If the foil in the area of 'bang' is really isolated from the rest of the house's foil, it might just have to be a case of rip the darned thing off in that porch area? :(
     
  8. Smokey

    Smokey Active Member

    Suggest contacting Kingspan Tec Support for advice, as they may well have come across before.
    And you'll be giving them valuable feedback if not:D
    Tel: +44 (0) 1544 387 382
    Fax: +44 (0) 1544 387 482
    Email: technical@kingspaninsulation.co.uk

    Your approval body eg NIC etc may have some useful advice too of course.
     
  9. dale76uk

    dale76uk Member

    retest your IR between Line and Foil with the switches in the Closed Position. That should give you and indication if the fault in on the Loops. Retest then with each switch drop closed one at a time. This will give you a clue to the room you need to be investigating. Did you carry out the IR with the Lamps removed?
     
  10. unphased

    unphased Screwfix Select

    Have you removed the area behind the black screw? That would be my first check. H e must surely have hit a cable with the screw. Keep your focus on that bit first before you go around removing all your boxes.
     
  11. I think Ian has said that they exposed the area where the screw went 'bang'. "When he took of radiator one of the screws was black so he thought that he had hit a cable behind the wall. He took a patch of plasterboard off but there was nothing behind but the screw had arced of the foil tripping the lighting circuit.No sign of cables, but blackened"

    From what he says, the screw arced across to the foil itself. He also says that the foil-backed board in that area (and where the fuse box is located) is very likely 'isolated' from the rest of the house's wallboards, so it would seem the worst they'd have to do is rip off a couple of sheets of board for a looksee.

    I hope he comes back to tell us what was found :)
     
    FatHands likes this.
  12. MGW

    MGW Screwfix Select

    This is an interesting case and it does show how Ali-tube may in the future become the norm rather than twin and earth. From the IET report on the Emma Shaw court case that also caused the fault to clear it's self after the plasters screw hit the cable. It was only when the plaster got wet when the fault was found again. However they also stated that the earth was lost so doing a test and inspection should have high lighted the fault. With that in mind I would be testing the ELI at all accessible points in the hope of finding which cable is involved.
     
    FatHands likes this.
  13. FatHands

    FatHands Well-Known Member

    Me too DA!
     
  14. Lectrician

    Lectrician Screwfix Select

    I don't believe so - Providing RCD protection was their attempt to address this type of fault.
     