Hi, If I am correct there should be an earth running from the Mains water into the house to the consumer unit? My mains water is about a 9 metre run from the consumer unit. There is a earth running between the pipes in the boiler cupboard (cold in from tank / hot out / cold out / heating) and back to the consumer unit. I have traced the mains from entry into the house to the tank in the loft and cannot find an earth anywhere, also the same on the mains run going to the kitchen. I guess there could of been one somewhere but it could of been cut off as there is a short earth coming out of the consumer box. So, I want to put one in. What size do I run fo rthe 9m run from pipe to CU?? Is 6mm big enough??
Are you sure your house isn't fed with plastic pipe? Is it quite modern or very old? Any earth's on the gas main?
You need to establish whether the cold water is an extraneous conductive part first. Is the incoming water pipe plastic or metallic?
The definition of an extraneous-conductive-part is “a conductive part liable to introduce a potential, generally earth potential, and not forming part of the electrical installation”. Thanks Google
If its indeed copper than enters from the ground then will almost certainly be an extraneous conductive part that requires bonding.
T.T. systems could be 6mm if memory serves, if its TN system with 100ASph then 10mm would be fine, even if the water main is plastic if it go's to copper then still needs bonding, and verifying of its connection.
So at 6mm @ 59p per metre and 10mm 97p per metre for my run of 10 metres I might as well spend the extra £4
Yes it depends on the earthing arrangement and can depend on the size of the suppliers neutral. For example if it was TN-C-S and the suppliers neutral was over 35mm then a 10mm bonding conductor wouldn't be adequate. Obviously 10mm will more than likely be adequate in the OP's case.
any Neutral conductor less than 35mm2 must be 10mm2 for a tncs, PME supply for a TT or such supply it must not be less than half the neutral conductor of the supply and must not be smaller than 6mm2. What supply installation do you have?