Hi All, I'm a new electrician so go easy, anyway after installing a fan to bathroom I then proceeded to carry out my basic tests for mwc. earth fault loop test fine, proceeded to test Rcd at end of circuit so as to be sure the circuit is protected as its in a special location, Connected leads and peformed 1x and got greater than 2000 ms, then tested on 5x and got greater than 40 ms, the test button works fine and it trips out at the socket outlet, p.s all switches were open. What am I doing wrong? Thanks
Leaving aside your question for a second an RCD is not supposed to be tested at the end of the circuit. It is the device you are testing and not the circuit. Ideally test at the terminals of the device with final circuit conductors disconnected.
As Risteard says, it is only the device that youa re testing. If you leave wires connected to the RCD, then there may be earth leakage on these attached conductors and this will skew/scrog/invalidate any tests that you are doing.
My Robin RCD trip time tester instrument comes with plug and iec connector - you plug it into sockets and do the trip sequence..I also purchased SL16 test lead for it, and have never had spurious readings (all readings within stipulated trip time parameters)
What if the circuit wasn't connected with an RCD up-front, but you thought it was? Testing the RCD 'solo' proves nothing about the circuit it should be protecting.
Ok Great, so we assume the RCD will trip under fault even though it was not tested at where I want protection, I,d still sleep easy knowing it tripped out at the business end
Blowed if I understand any of it. I've always tested at socket and other positions, and never had a problem.
I think I understand Sen. You test the rcd directly to prove it works properly. So you test the eli, and continuity, and ir - and as long as these pass then the rcd must operate correctly?
So why on an EIC is there any need to record the disconnect times for each circuit? You could just test all RCD's once on the board without connecting anything, regardless of which circuit their eventually supplying?
I think I will carry on as I have always done it..but will also test rcd directly before plugging in tester to various parts of the circuitsl