Shower switch neutral melted

Discussion in 'Electricians' Talk' started by Alex_1990, Apr 27, 2024.

  1. Alex_1990

    Alex_1990 New Member

    Was showering this evening and smelled burning plastic. Immediately switched the shower off. Done a bit of sniffing about and smelled it from the pull chord switch. Turns out the supply side neutral had melted. What could have caused this? I've attached a pic
     

    Attached Files:

  2. arrow

    arrow Screwfix Select

    Loose connection
     
    Ind spark and LearnMore like this.
  3. Comlec

    Comlec Screwfix Select

    Common problem caused by poorly terminated cable or incorrectly torqued connection.
    Over time you get a little arching that soon causes that problem.

    Easy fixed.
    1. Buy a quality isolator switch
    2. Ensure you have clean copper going into the terminals.
    3. Tighten the terminals to the correct torque.

    Good luck with your repair.
     
  4. Ind spark

    Ind spark Screwfix Select

  5. Alex_1990

    Alex_1990 New Member

    So will it be safe enough to cut back the cable a bit or should I look for further melting further back in the attic?
     
  6. longboat

    longboat Screwfix Select

    Yes, very common problem these days. Shower wattage has increased and the quality of the switches has decreased.
     
    WH55 likes this.
  7. Comlec

    Comlec Screwfix Select

    Once you see clear copper and no heating on the insulation you will be fine.
     
    Alex_1990 likes this.
  8. Alex_1990

    Alex_1990 New Member

    Thanks. Just wanted to be sure before I wired a new switch. Going to use the crabtree one instead of the LAP switch that was on there. The wires seemed very cramped in.
     
  9. Comlec

    Comlec Screwfix Select

    These switches are designed to be used to isolate the shower. If you use them as functional switches (on and off each time you shower) then this can shorten their life.
     
    longboat and Alex_1990 like this.
  10. arrow

    arrow Screwfix Select

    If you can cut out a 47mm deep double box and fit a larger sized isolator. It makes terminating easier and more room.
     
  11. arrow

    arrow Screwfix Select

    Great pull switches
     
    Ind spark likes this.
  12. Bazza

    Bazza Screwfix Select

    That may have been the original problem.
    Budget range product + high current = problems !
     