URGENT CAN WATER MAIN & ELECTRIC SUPPLY GO TOGETHER

Discussion in 'Electricians' Talk' started by DHK, Jun 5, 2004.

  1. DHK

    DHK New Member

    Please can you help we have a digger in this weekend digging a trench to put in Water & Electric supplies to the end of our garden as it is over 200ft to save keep reeling out cables and hoses. We have dug to 750mm for the water and just realised that we have misjudged the quantity of ducting (blue for water and black for electric, crinkled ducting as used by ground workers) we have ordered. We must finish this weekend to return the digger on monday and can't get the digger out of the garden without finishing the job.

    So can anyone tell us if it is acceptable to run both the water and electric supply in ONE piece of ducting as long as it is at 750 to meet the regulations for the depth of the water supply.

    Thanks
     
  2. unphased

    unphased Screwfix Select

    Kel

    No you should not put cable and pipework in the same duct. You can put the pipework and cable in the same trench but you must put them at different depths and use yellow warning tape laid over the cable duct to warn of Cables Below. Your groundworker should know all this if he is worth his salt.

    Roy
     
  3. unphased

    unphased Screwfix Select

    Just a thought. Is the pipework for your water blue MDPE? And are you using steel wire armoured cable?? If so you need not put this in duct! Just put the water pipe in trench and lay the swa separately. Just a thought. If its your own private garden there is no hard and fast rule for laying the services in duct. It would be different if in a highway. 750mm depth is good for both the water and the electric. You should be okay if its like that and means you can get the job finished. Best to surround the cable in sand too.

    Roy
     
  4. DHK

    DHK New Member

    Thanks Roy

    Yes the water is blue MDPE.

    The eletric was going to be normal 8mm cable run to the garage (into a fuse box) then out of the garage in 4mm to our shed/summerhouse at the bottom of the garden which would just have a socket and a light. This is why we were planning on putting the electric as well as the water in ducting.

    Kel
     
  5. unphased

    unphased Screwfix Select

    Yes the water is blue MDPE.

    The eletric was going to be normal 8mm cable run to
    the garage (into a fuse box) then out of the garage
    in 4mm to our shed/summerhouse at the bottom of the
    garden which would just have a socket and a light.
    This is why we were planning on putting the electric
    as well as the water in ducting.

    Kel

    Not sure that you have the electric arrangement designed properly. Have you got RCD's? Consumer unit at shed end? Would you like some assistance?

    I would just lay the MDPE directly in to the trench and use the duct for your cables. If you are plannning on pulling the cables through remember to put draw cords in or you will never get the cables through! I would strongly recommend that you consider swa. It will last longer and be safer. Post a reply with your current plan of action and we can help. ;)

    Roy
     
  6. DHK

    DHK New Member

    Hi Roy

    Thanks for all this help, we are 1st time buyers at 40years old and are having to do all the work to our run down house ourselves as we have run out of fiances. Hubby started as an apprentice electrician almost 20 years ago but it never worked out and he changed to an autoelectrician. So he has some knowledge but he is a bit rusty on it nowdays. At the moment he is the digger driver as well as having to do all the other jobs.

    I take your message down to him and then come back to you shortly. Once again thank you.
     
  7. plugwash

    plugwash New Member

    go to an electrical wholesaler and buy some nice big amroumed cable
    200ft is about 60m afaict so for a 40A feed (which is what i find is generally advised for outbuilding suppllies) you need to be using 16mm (due to volt drop)

    the armoured cable can be run directly in the ground eliminateing the need for ducting

    only problem i can see is getting it on a sunday maybe one of the sparkys here would sell you some (at a significant markup ofc ;) ) the parts other than the cable can be purchased later

    using the same size cable for the whole outdoor run is probablly less hassle and keeps the calculations simpler

    start from a 40A breaker in the non rcd side of the house CU

    from here run in 10mm twin and earth to a metalclad 2 module din rail box with a 40A rcd fitted

    in the garage gland both the cables into a big metal adaptable box and inside this fit henly blocks to join the 2 runs of SWA and the tails to a CU (the adaptable box is needed because the single insulated individual cores from the SWA must not be exposed

    from here run with the 16mm armoured to a metalclad switch CU in the garage



    from here run a lighting cuircuit from a 6A mcb a ring from a 32A mcb

    in the shed fit another switched metalclad CU and run another ring and lighting cuircuit
     
  8. plugwash

    plugwash New Member

    ok corrected version

    go to an electrical wholesaler and buy some nice big amroumed cable
    200ft is about 60m afaict so for a 40A feed (which is what i find is generally advised for outbuilding suppllies) you need to be using 16mm (due to volt drop)

    the armoured cable can be run directly in the ground eliminateing the need for ducting

    only problem i can see is getting it on a sunday maybe one of the sparkys here would sell you some (at a significant markup ofc ) the parts other than the cable can be purchased later

    using the same size cable for the whole outdoor run is probablly less hassle and keeps the calculations simpler

    start from a 40A breaker in the non rcd side of the house CU

    from here run in 10mm twin and earth to a metalclad 2 module din rail box with a 40A rcd fitted

    from here run with the 16mm armoured to the garage

    in the garage gland both the cables into a big metal adaptable box and inside this fit henly blocks to join the 2 runs of SWA and the tails to a CU (the adaptable box is needed because the single insulated individual cores from the SWA must not be exposed

    run with 10mm twin and earth from this adaptable box to a metalclad CU in the garage

    from here run a lighting cuircuit from a 6A mcb a ring from a 32A mcb

    in the shed fit another switched metalclad CU and run another ring and lighting cuircuit
     
  9. DHK

    DHK New Member

    Here goes Roy I am going to try to layout a diagram using text only and maybe you can tell us where we are going wrong.
    ======================================================
    Consumer unit in house on 1st floor to back of house at ground level is 15 metres. Want to take feed from here to garage.
    /
    /
    Back of house to garage is 20 metres. We want to fit another consumer unit in garage with RCD's to give protection to garage, shed & garden. So in total from consumer unit in the house to the consumer unit in the garage would be approximately 35 metres. We want to take a feed from the comsumer unit in garage to shed/summerhouse. Hubby will want to use power tools in the garage.
    /
    /
    Garage to shed/summerhouse is approx 50 metres. In shed/summerhouse we want to have a double socket for plugging in garden equipment like strimmer or shredder or maybe small electrical appliance if having a barbeque. Also a single socket to power a light (flu probably) to save running a lighting curcuit as well.

    I hope this makes sense.
     
  10. DHK

    DHK New Member

    Hi Roy

    UPDATE

    We have just managed to borrow some ducting from a neighbour and should have enough now to run both the water and electric in SEPERATE ducting. The last part of the water will have to be in black ducting rather than blue but at least it will be protect in our stoney soil.

    Can we still take you up on your offer of help with the electric arrangment design, please see my earlier message for details showing our measurements.

    With regard to the depths we know it should be 750mm water and 450mm electic but could we put them both at 750mm. My reasoning is that we may use a cultivator on the land above some of the ducting in the future and I am concerned that 450mm will be deep enough. The cultivator should only go to about 300mm but that does not leave much tollerance if it suddenly dug in deeper.

    With regard to still using swa even in the ducting is this essential. We have looked at my husbands usual suppliers (Contact-Basildon and QVS-Basildon) and it is very expensive for such a long run especially in 16mm as someone else recommended and Screwfix don't do 16mm or long rolls. We live in Tolleshunt D'Arcy, Essex which is near Maldon and Colchester if you can recommend anyone cheaper.

    Thanks so much for your help.
    Kel
     
  11. plugwash

    plugwash New Member

    i would still use the 16mm armoured though in the way i specified before

    maybe its just me but i don't really trust ducting

    you need the 16mm because of the insane lengths involved (and the insanely small allowed volt drop in uk electrical regs)
     
  12. unphased

    unphased Screwfix Select


    Can we still take you up on your offer of help with
    the electric arrangment design, please see my earlier
    message for details showing our measurements.


    Good morning Kel, Plugwash has given some sound advice in his post. Look at carefully and see if there is anything you could use.

    With regard to the depths we know it should be 750mm
    water and 450mm electic but could we put them both at
    750mm.


    Yes that would fine. Keep the ducts apart and put both in the bottom of the trench. As you say the depths quoted are minimum and no harm going deeper!

    With regard to still using swa even in the ducting is
    this essential
    . ...is very expensive for such a long run especially in
    16mm as someone else recommended and Screwfix don't
    do 16mm or long rolls. We live in Tolleshunt D'Arcy,
    Essex which is near Maldon and Colchester if you can
    recommend anyone cheaper.
    >

    Well according to my calculations at 40A you could get away with 10mm armoured as this would be good for 52m. (6mm armoured is only good for 31.5m).

    As previously advised you should really use swa for the best job. pvc cables in duct would be more susceptible to groundwater long term. I would suggest using a 32A breaker in the fuseboard instead of a 40A for the outside circuit supply. This should be ample taking diversity in to account and this will get your cable size down to 10mm comfortably (and this should be much cheaper than 16mm.)

    Using a 32A breaker to protect the circuit allows you up to 65m of cable at 10mm for voltage drop compliance.

    Roy
     
  13. unphased

    unphased Screwfix Select


    Consumer unit in house on 1st floor to back of house
    at ground level is 15 metres. Want to take feed from
    here to garage.

    Back of house to garage is 20 metres. We want to fit
    another consumer unit in garage with RCD's to give
    protection to garage, shed & garden. So in total from
    consumer unit in the house to the consumer unit in
    the garage would be approximately 35 metres.


    Okay thats no problem. Use a 40A breaker in the fuseboard and 16mm T&E to get to the garage. This is necessary to limit volt drop from house to the garage as you are going to need max voltage at garage befire you continue cable up to the shed/summerhouse.

    to take a feed from the comsumer unit in garage to
    shed/summerhouse. Hubby will want to use power tools
    in the garage
    .

    > Garage to shed/summerhouse is approx 50 metres. In
    shed/summerhouse we want to have a double socket for
    plugging in garden equipment like strimmer or
    shredder or maybe small electrical appliance if
    having a barbeque. Also a single socket to power a
    light (flu probably) to save running a lighting
    curcuit as well.
    >

    Yes that all looks good. As my previous post I would definitely use 10mm to get up the garden as you are not going to be using very much current at all. As its a job you only do once 10mm gives plenty of scope to expand at shed if you need and 16mm is overkill so I think we've sorted it.

    Kel I am going out doing leaflet drops now so wont be around for a few hours. Good luck and hope you get it all finished.

    Roy
     
  14. unphased

    unphased Screwfix Select

    Use a 40A breaker in the
    fuseboard and 16mm T&E to get to the garage. Then use a 32A breaker at the garage CU for the cable going to the shed.
     
  15. DHK

    DHK New Member

    <u></u>Hi Roy and Plugwash.

    A really big thank you from me and hubby for the help and advice. We only got 5 hours sleep but we are on track now.

    We now have both the water and electric ducting in place and the water supply pushed through and tee'd off where it needed to go. We have 2 strings pulled through the electric ducting so that we can pull the cables through at a later date when we can get what you have adviced.

    So very shortly we can start to back fill. I can't thank you enough guy's.

    Kel
     
  16. Lectrician

    Lectrician Screwfix Select

    Ducting is the way, even if you have the cable ready!!
     
  17. DHK

    DHK New Member

    Just to let you know we are just back indoors and the diggers back at the front of the house. All digging and ducting work is completed. We will need the digger back to landscape the mess in the garden but thanks to you guys it can go back tomorrow until we are next off work saving us a fortune in extra hire costs.

    Thanks Kel
     