What to do with Earth when installing double insulated downlights

Discussion in 'Electricians' Talk' started by Pete Hanbury, Jul 17, 2016.

  1. Pete Hanbury

    Pete Hanbury New Member

    Hi,

    I'm guessing this has been asked before but...

    I'm going to replace a single pendent light with a set of down lights. The new lights are double insulated so don't require the earth and don't have a terminal for it either. I'm intending on connecting the lights using the original cables for the pendent and then looping from one to the next. I'll connect the earth using a separate terminal block and then insulate but the question is, what do you do with the earth when you get to the final light since it's at the end of the line and not looped back? Does it need to be taken back to the original junction box (i.e completing the continuity) or can it be terminated in an insulated junction block?

    Thanks in advance...
     
  2. I'm not a sparky, so caution...

    Light wiring - like those on the sockets - are generally carried out in two ways - a 'ring' (which has the main power cable coming out of the CU, going around all the sockets in that circuit, and then returning to the same connection in the CU), and a radial (which means single cables heading to the lights and daisy-chaining).

    Lightings circuits are almost always 'radial', so the supply cable will loop from light to light before ending at the last one on that circuit.

    So, if the power cable to that last light ends at that last light, then the earth wire can do so too. Just terminate it as you suggest.

    But pros will confirm - I hope...
     
  3. tore81

    tore81 Screwfix Select

    connector block taped up

    Or left in sleeving bent over with no copper on show.

    See what sparks say
     
  4. KIAB

    KIAB Super Member


    A ring final circuit for lighting is a total waste of cable,in fact it's is unusual, haven't seen one in years in domestic wiring.
    And I wouldn't not consider using a ring final myself for lighting,when I was at college many years ago,it was not considered good practice in to wire lighting circuits as a ring final, because of problems breaking the ring.

    Don't know if the views on lighting circuits being ring final today has changed, some spark on here will comment on that.

    Domestic lighting circuits are usually radial, so just terminate the earth in the last fitting.
     
    Last edited: Jul 17, 2016
  5. Rulland

    Rulland Screwfix Select

    Continue the earth through all the fittings and just 'park' it at the end one.
    The earth protects the cable/circuit as well as anything connected to it even if the fittings are double insulated.
    It also means the earth is there if the fittings are ever changed in future to ones requiring an earth.
    The amount of times I see the earth's just chopped because the person fitting them thinks they're not needed is unbelievable.
     
    tore81 and KIAB like this.
  6. tore81

    tore81 Screwfix Select

    What do you mean by park it Rulland. I was told to fold over and leave in earth sleeving and out the way
     
  7. KIAB

    KIAB Super Member

    I just terminate it, I suppose park it, means the same, in a small terminal block.

    Agree Rulland, it's so infuriating seeing earth wire sniped off.:mad:
     
    tore81 and Rulland like this.
  8. Rulland

    Rulland Screwfix Select

    That's it mate, or in a choccy block, it's there, but accessible if required in the future.
     
    tore81 and KIAB like this.
  9. Rulland

    Rulland Screwfix Select

    Posted at the same time as Mr Kiab :)
     
    KIAB likes this.
  10. peter palmer

    peter palmer Screwfix Select

    Is this the type of downlights that have that crappy 2 way connector on the top with a flimsly plastic lid.

    [​IMG]

    What you should really do is take a short piece of twin flex from the fitting into a suitable joint box and continue the earths in the JB. Personally if doing it this way a just use a small 20A joint box, others will say that horrific as its got no strain relief on the cables and wont be fastened down, I say as long as the monster that lives under the floor doesn't play with them they will be fine.
     
  11. KIAB

    KIAB Super Member

    That is only fit for the bin.:)
     
  12. Rulland

    Rulland Screwfix Select

    Unfortunately there is a fallacy that the live conductors are the most important, ie, without them the light or whatever won't work.
    The circuit protective conductor, cpc, is actually the most imperative one to get correct, this is what affords protection during fault conditions etc and could save your life, again, most people do not realise that.
     
    philthespark, KIAB and tore81 like this.
  13. stateit

    stateit Screwfix Select

    I use Wago boxes exclusively these days when there's only a few cables or so involved: Maintenance free, provide strain relief and fit through a downlight hole. No need for a screwdriver at all (better when you're up a ladder).
     
    TP&N, Rulland, tore81 and 1 other person like this.
  14. TP&N

    TP&N Active Member

    I carry a cpc to every fitting required or not remember the poor gizzer thats going to carry out the next EICR will need it for earth loop.
     
  15. spinlondon

    spinlondon Screwfix Select

    What you should do, is terminate all 3 conductors into chocolate blocks in an enclosure. Then using some 2 core flex wire from the enclosure to the fitting.
    Alternatively, you could try to terminate the live conductors in the fitting, and sleeve and terminate the earth conductor into a chocolate block.
     
    nffc likes this.
  16. philthespark

    philthespark Active Member

    Many many years ago when I was an apprentice I read something in a book that has stayed with me.It said that when wiring anything you should always make the earth wire the longest so that in the event of a pull on the cable the earth would be the last to go,as you say it's the most important wire,yes without the live or neutral a thing won't work,without a correctly functioning earth there's nothing stopping that piece of kit killing you if it goes wrong.
     
    tore81 and Rulland like this.
  17. Pollowick

    Pollowick Screwfix Select


    Ban ChocBlocks!

    An Ashley/Hager J803/804 is the way to go. A decent enclosure with Wago connectors, feed in (LN&E), feed out to next J803/4 and two feeds through 2 core flex to two fittings
     
  18. tina lucinda lane

    tina lucinda lane Screwfix Select

    nothing wrong with terminal block (choc bloc) when fitted right and checked regularly
     
  19. Pollowick

    Pollowick Screwfix Select

    How many have you come across that are NOT fitted correctly? and how often do you check what is there? And how many poorly made blocks are out there?

    For the small extra cost a J803/4 is a lot easier to use. The quality is built in.
     
  20. Bazza-spark

    Bazza-spark Screwfix Select

    Correct. Live the shortest so it pulls out first, earth the longest so it maintains protection until last.

    Kind regars
     
    philthespark likes this.