How you can say 4D5A is not the table to use for flat twin and earth cable? Good god man.... I'm not I'm saying THERMAL AND SOUND INSTALLATION One of the features of a modern dwelling is the requirement in Parts E and L to meet the thermal and sound deadening requirements of the Building Regulations. The IEE recently carried out some work to determine specific ratings for twin with earth cables when insulated in a thermally insulated wall see table 4D5A of BS7671, table 6F of the On Site Guide
I said 4D5A was the table to use, you said it was not the one to use, and that 4D2A (or was it 4D1B?) was more appropriate, and then when I pointed out that everywhere you look it says 4D5A, you quoted an article which says 4D5A...
If you're a shower manufacturer, and you're giving advice on cable sizes, and don't want to confuse your customers by talking about installation methods, what can you do except take the worst case figures from the tables published in the regs or the OSG?
Back to the 'original' point, I changed a CU last week and was also asked to upgrade the Shower cable to 10mm T&E, the customer was going to fit a 9.6KW shower.. The cable length to the shower (via pull cord) was 3 metres ))..(6mm T&E), clipped direct (RM1 46A). I told him no upgrade was required and fitted a 40A mcb (via the RCD side of the split CU).. Correct, as per table 4D2A..?
Mind if I laugh ? :O:^O:^O Mr. HandyAndy - really well either share the joke with us all thats so funny or contribute something usefull to the disussion... Or perhaps you know nothing again :^O Mr Fooman - Really Really Really I AM sharing the joke. And laughing at it. Seems I'm not the only one who doesn't know what they're talking about. This thread, looks like one that I could have dreamed up. Yes it is. No it isn't. But, but, but......... Mr. HandyAndy - really
I said 4D5A was the table to use, And I said that 4D5A was not the correct table My references to 4D5A was in context in its correct use.. which is not as it being the default table.
Are you going to go wrong using 4D2A? No, the ratings are the same or lower. Does this matter in practice? It might, if you followed it strictly, and found that you couldn't use 2.5mm² for a ring final, when if you'd used 4D5A you could. Does it mean that 4D5A is not the correct table to use for flat twin & earth? No.
Copy & Paste It should however be noted that for PVC sheathed flat cables two current rating tables are given 4D2A and 4D5A. 4D5A should be used where Reference Method 1 is applicable, AND where these cables are in contact with thermal insulation on one side (Installation Methods 6 and 15). 4D2A should be used for other applications including where Reference methods 3 and 11 are applicable. Is it clear now ?
Q: 4D5A is the table to use to look up the current carrying capacity of flat twin & earth cable. a) YES [ ] b) NO [ ]