Shower Cable - to be 6mm2?

Discussion in 'Electricians' Talk' started by Leoric, Jan 12, 2007.

  1. ban-all-sheds

    ban-all-sheds New Member

    I'm not trying to be funny - I'd love to know where that quote is from, and the context, but so far all I've got to go on are the words in the regs and the OSG, which say that 4D5A is for flat twin/earth, and the words in the Wiring Matters article on Amendment 1 which explicitly say that 4D2A is based on round cables....
     
  2. X

    X New Member

    I'm not trying to be funny

    Please keep reading the pdf ...1st few paragraphs

    The reasons for the table 4D5A and when it should be used instead of 4D2A should become clear.

    You will see that 4D2A is mentioned in connection with 2.5mm T&E and that the issue was with thermal insulated walls... the issues also arose because the figures were based upon results using round cables... thus 4D2A is used for T&E

    Thats figures based upon... not for.
     
  3. ban-all-sheds

    ban-all-sheds New Member

    Assuming that we are talking about the same PDF document, what that says is that the figures in 4D2A were based on the performance of round cables, and that the Electrical Research Association were asked to measure the rating of the standard UK flat twin with earth insulated and sheathed cables, and that they did so, and got different results and so a new table, 4D5A, was created to provide the results for standard UK flat twin with earth insulated and sheathed cables...
     
  4. X

    X New Member

    Your missing out....

    Under what circumstances was 4D2A found to be incorrect.
     
  5. ban-all-sheds

    ban-all-sheds New Member

    All of them.

    1) Someone spots that the old ratings, in 4D2A, meant that in extremis 2.5mm² would not be OK for a ring final.

    2) "Oo err, we'd better look into this properly. ERA - we understand that 4D2A is based on the performance of round cables, will you please run some tests using UK flat twin & earth cables?"

    3) "OK, IEE, we have done those tests, and we get different results for UK flat twin & earth cables. Here they are."

    4) "Thank you, ERA. We will publish these new figures for the ratings of UK flat twin & earth cables in a new table, 4D5A, as part of an amendment to the Wiring Regulations.
     
  6. ban-all-sheds

    ban-all-sheds New Member

    Where is

    It should however be noted that for PVC sheathed flat
    cables two current rating tables are given 4D2A and
    4D5A. > 4D5A should be used where Reference Method 1
    is applicable, AND where these cables are in
    contact with thermal insulation on one side
    (Installation Methods 6 and 15). 4D2A should
    be used for other applications including where
    Reference methods 3 and 11 are applicable.

    from?
     
  7. MRWONG006

    MRWONG006 New Member

    You got that Leoric. Another Pole you lot just helped.
     
  8. 2 wheeled ant

    2 wheeled ant New Member

    1) Someone spots that the old ratings, in 4D2A, meant
    that in extremis 2.5mm² would not be OK for a
    ring final.


    RM are the only circuits you dont need to design!
    So dont worry
    A1 A2 & A3 circuits
    Ant
     
  9. X

    X New Member

    Ok BAS ... another day lets try another method

    The original poster stated how the cable was run to the shower..

    What reference method do you think it is ?

    Can you find it on the table you wanted to use ?
     
  10. ban-all-sheds

    ban-all-sheds New Member

    "Cable already fitted is 6mm2, loosley fitted in brickwork".

    "Loosely fitted in brickwork" is a bit like being embedded and/or a bit like being clipped to the surface of brickwork.

    Table 4A1.

    <u>Open and clipped direct</u>.

    Installation method 1. Sheathed cables clipped direct to or lying on a non-metallic surface. Appropriate Reference Method for determining current carrying capacity: Method 1.


    <u>Cables embedded directly in building materials</u>.

    Installation method 2: Sheathed cables embedded directly in masonry, brickwork, concrete, plaster or the like (other than thermally insulating materials). Appropriate Reference Method for determining current carrying capacity: Method 1.

    So "loosely fitted in brickwork" would seem to be Reference Method 1.


    Table 4D5A.

    Column 4. Reference Method 1. 6mm² 47A.
     
  11. Ant1981

    Ant1981 New Member

    Nice to see someone else backpeddling for once :^O
     
  12. X

    X New Member

    In general... I'd of more prefered the example picture of voids in Installation method 16 giving ref method 4.
     
  13. X

    X New Member

    Or even ref method 3 if the greater % of the cable run complys...

    Neither of which are available in 4D5A

    If in doubt.. use 4D2A (look at the ratings and see why)
     
  14. MRWONG006

    MRWONG006 New Member

    Re: Shower Cable - to be 6mm2?
    Posted: Jan 12, 2007 4:58 PM Reply


    I was referring to this table



    Standard Shower Rating

    Watts (kW)
    Maximum load from the supply

    A
    Maximum size of Protective device
    Recommended

    Minimum

    Cable Size to be Used
    Recommended

    Protective Device

    6000 (6kW)
    26
    32A
    6mm2
    RCBO

    6500 (6.5kW)
    28.2
    32A
    6mm2
    RCBO

    7000 (7kW)
    30.4
    32A
    6mm2
    RCBO

    7500 (7.5kW)
    32.6
    40A
    10mm2
    RCBO

    8000 (8kW)
    34.7
    40A
    10mm2
    RCBO

    8500 (8.5kW)
    36.95
    40A
    10mm2
    RCBO

    9000 (9kW)
    39.13
    40A
    10mm2
    RCBO

    9500 (9.5kW)
    41.3
    45A
    10mm2
    RCBO

    10,000 (10kW)
    43.47
    45A
    10mm2
    RCBO

    10,500 (10.5kW)
    45.65
    50A
    16mm2
    RCBO

    11,000 (11.0kW)
    47.82
    50A
    16mm2


    All data in this table has been compiled with
    reference to BS7671: 2001. The IEE Wiring Regulat

    Cable Data taken from Table 4D2A. Page 222.



    Why does'nt the 11.0 KW need a RCBO but all the others do ?

    I would say because you can&#146;t buy an 11kw Shower? On the market now is a 10.8kw
     
  15. Ant1981

    Ant1981 New Member

    Actually, it doesn't need an RCBO, so long as the Zs allows a disconnection time of 0.4s, which most radials for a shower will do. Who gave you that information? Certainly not BS7671.
     
  16. X

    X New Member

    The makers of the showers sometimes mention that a rcd is needed or something like that..

    IMHO its a cop out for them being held liable if the naked doris gets fried in the shower
     
  17. Ant1981

    Ant1981 New Member

    Agree.
     
  18. Mr. Handyandy

    Mr. Handyandy Screwfix Select

    RCD/no RCD ?


    Which is safer(for the person in the shower)with certain eventualities considered ?



    Mr. HandyAndy - really
     
  19. Ant1981

    Ant1981 New Member

    Why would you fit an RCD?
     
  20. Mr. Handyandy

    Mr. Handyandy Screwfix Select

    Why would you fit an RCD?


    Is that question specifically to me ?


    Er, for one, in case the water inadvertently made a live cable pass electricity to the shower fitment, and possibly, me.

    I'd like to know that if I were an earth path, that I would not be an earth path for very long, without dying.



    Mr. HandyAndy - really
     